A service raceway enters an enclosure through a knockout with concentric rings left in place. Which bonding method alone is NOT acceptable?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5049
- A: A standard locknut only
Explanation
Service raceways must be bonded by threaded connections, threadless couplings made tight, bonding jumpers, or other listed devices. Bonding jumpers are required around impaired connections such as concentric or eccentric knockouts, and a standard locknut alone is not sufficient. See 250.92(B).