For a separately derived system, where is the system bonding jumper installed under the general rule?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5054
- B: At one point only, from the source to the first disconnect
Explanation
The system bonding jumper connects the grounded conductor to the supply-side bonding jumper or enclosure at any single point between the source and the first system disconnecting means. Installing it in more than one place creates parallel neutral paths. See 250.30(A)(1).
More questions: Grounding and Bonding
- 5055A transformer supplies 250 kcmil copper secondary conductors. What is the minimum copper GEC for this separately derived system?
- 5056The system bonding jumper of a separately derived system is sized based on
- 5057A detached garage supplied by a feeder must have a grounding electrode system, except where it is supplied by
- 5058At a separate building supplied by a feeder that includes an EGC, the grounded conductor at the building disconnect must be
- 5059Which of these AC systems is required to be grounded?
- 5060High-impedance grounded neutral systems are permitted for 3-phase AC systems of 480 V to 1000 V where