Question 5057 of 790 · California General Electrician Exam

A detached garage supplied by a feeder must have a grounding electrode system, except where it is supplied by

Exactly one answer is correct.

Show solution

Correct answer to question 5057

  • A: A single branch circuit, including a multiwire one, with an EGC

Explanation

A separate building needs its own grounding electrode system unless it is supplied by only one branch circuit, which may be multiwire, that includes an EGC. See 250.32(A).

Next to question ›