Question 5062 of 790 · California General Electrician Exam
An equipment bonding jumper on the load side of an OCPD is sized according to
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5062
- B: Table 250.122 based on the largest OCPD supplying the circuits
Explanation
Load-side equipment bonding jumpers are sized from Table 250.122 based on the rating of the largest OCPD supplying circuits within the raceway or enclosure. See 250.102(D).
More questions: Grounding and Bonding
- 5063A supply-side bonding jumper on the line side of the service disconnect is sized from
- 5064In NEC 2020 and NEC 2023, grounding requirements specific to systems over 1000 V are located in
- 5001At a building or structure, which of the permitted grounding electrodes must be bonded together to form the grounding electrode system?
- 5002A metal underground water pipe qualifies as a grounding electrode only if it is in direct contact with the earth for at least what length?
- 5003When a metal underground water pipe is used as a grounding electrode, what else does the Code require?
- 5004Under the general rule, interior metal water piping located more than what distance from its point of entrance may NOT be used to interconnect electrodes that are part of the grounding electrode system?