Question 5061 of 790 · California General Electrician Exam
Which of the following shall NOT be used to connect EGCs or bonding jumpers to enclosures?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5061
- A: Sheet metal screws
Explanation
Sheet metal screws are prohibited for connecting grounding and bonding conductors to enclosures. The other methods are recognized connection means. See 250.8.
More questions: Grounding and Bonding
- 5062An equipment bonding jumper on the load side of an OCPD is sized according to
- 5063A supply-side bonding jumper on the line side of the service disconnect is sized from
- 5064In NEC 2020 and NEC 2023, grounding requirements specific to systems over 1000 V are located in
- 5001At a building or structure, which of the permitted grounding electrodes must be bonded together to form the grounding electrode system?
- 5002A metal underground water pipe qualifies as a grounding electrode only if it is in direct contact with the earth for at least what length?
- 5003When a metal underground water pipe is used as a grounding electrode, what else does the Code require?