Correct answer to question 5058
- B: Kept isolated from the EGC and enclosure
Explanation
Where an EGC is run with the feeder, the grounded conductor at the separate building may not be connected to the EGC or the grounding electrode system. The EGC is connected to the building electrode system. See 250.32(B)(1).
More questions: Grounding and Bonding
- 5059Which of these AC systems is required to be grounded?
- 5060High-impedance grounded neutral systems are permitted for 3-phase AC systems of 480 V to 1000 V where
- 5061Which of the following shall NOT be used to connect EGCs or bonding jumpers to enclosures?
- 5062An equipment bonding jumper on the load side of an OCPD is sized according to
- 5063A supply-side bonding jumper on the line side of the service disconnect is sized from
- 5064In NEC 2020 and NEC 2023, grounding requirements specific to systems over 1000 V are located in