A transformer supplies 250 kcmil copper secondary conductors. What is the minimum copper GEC for this separately derived system?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5055
- C: 2 AWG
Explanation
The GEC for a separately derived system is sized from Table 250.66 based on the derived ungrounded conductors. 250 kcmil copper is over 3/0 through 350 kcmil, so 2 AWG copper is required. See 250.30(A)(5).