An insulated conductor 4 AWG or larger may be permanently identified as an EGC at installation by
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5048
- D: Marking it green at each end and accessible points
Explanation
Conductors 4 AWG and larger may be identified at each end and every point where accessible by stripping the insulation, coloring the insulation green, or marking it with green tape or adhesive labels. See 250.119(A).
More questions: Grounding and Bonding
- 5049A service raceway enters an enclosure through a knockout with concentric rings left in place. Which bonding method alone is NOT acceptable?
- 5050The intersystem bonding termination must be able to connect at least how many intersystem bonding conductors?
- 5051Where is the intersystem bonding termination required?
- 5052A service has 3/0 AWG copper ungrounded conductors. What is the minimum copper bonding jumper for the interior metal water piping?
- 5053Metal gas piping that is likely to become energized may be bonded by
- 5054For a separately derived system, where is the system bonding jumper installed under the general rule?