A service has 3/0 AWG copper ungrounded conductors. What is the minimum copper bonding jumper for the interior metal water piping?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5052
- D: 4 AWG
Explanation
The metal water piping bonding jumper is sized from Table 250.102(C)(1) based on the service conductors. For 2/0 or 3/0 copper the jumper must be at least 4 AWG copper. See 250.104(A).
More questions: Grounding and Bonding