Which identification is NOT permitted for an equipment grounding conductor of 6 AWG or smaller?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5047
- C: Gray insulation
Explanation
An EGC may be bare, covered, or insulated, and if covered or insulated must be green or green with one or more yellow stripes. Gray is reserved for grounded conductors. See 250.119.