The intersystem bonding termination must be able to connect at least how many intersystem bonding conductors?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5050
- B: 3
Explanation
The intersystem bonding termination must have the capacity for connection of not less than three intersystem bonding conductors. See 250.94.