Question 5045 of 790 · California General Electrician Exam
Why is the earth not permitted as the effective ground-fault current path?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5045
- A: Its impedance is too high to make OCPDs trip reliably
Explanation
The earth has high impedance, so a ground fault through earth may not draw enough current to open the OCPD. The Code requires a low-impedance metallic path instead. See 250.4(A)(5).
More questions: Grounding and Bonding
- 5046A ground rod is driven at a parking lot light pole and connected to the pole. How does the Code treat this rod?
- 5047Which identification is NOT permitted for an equipment grounding conductor of 6 AWG or smaller?
- 5048An insulated conductor 4 AWG or larger may be permanently identified as an EGC at installation by
- 5049A service raceway enters an enclosure through a knockout with concentric rings left in place. Which bonding method alone is NOT acceptable?
- 5050The intersystem bonding termination must be able to connect at least how many intersystem bonding conductors?
- 5051Where is the intersystem bonding termination required?