Question 4088 of 790 · California General Electrician Exam

A branch circuit supplies a continuous load of 16 amperes and no noncontinuous load. What is the minimum conductor ampacity before any adjustment or correction?

Exactly one answer is correct.

Show solution

Correct answer to question 4088

  • D: 20 amperes

Explanation

210.19 requires branch circuit conductors to have an ampacity of at least 125 percent of the continuous load plus 100 percent of the noncontinuous load. 16 A x 1.25 = 20 A.