For branch circuit sizing, a continuous load is one where the maximum current is expected to continue for how long?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4090
- B: 3 hours or more
Explanation
Article 100 defines a continuous load as one where the maximum current is expected to continue for 3 hours or more. Such loads trigger the 125 percent sizing rules of 210.19 and 210.20.
More questions: Branch Circuits, GFCI and AFCI