In a dwelling living room, what may substitute for the required wall-switch-controlled lighting outlet?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4098
- D: One or more receptacles controlled by a wall switch
Explanation
210.70(A)(1) requires at least one wall-switch-controlled lighting outlet in every habitable room. An exception permits one or more wall-switch-controlled receptacles instead, except in kitchens and bathrooms.