Question 4104 of 790 · California General Electrician Exam
What is the ampacity of a 6 AWG copper THWN conductor in the 75 C column of Table 310.16?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4104
- A: 65 amperes
Explanation
6 AWG copper is listed at 55 A at 60 C, 65 A at 75 C and 75 A at 90 C. THWN is a 75 C insulation, so 65 A applies.
More questions: Branch Circuits, GFCI and AFCI
- 4105A 30-ampere branch circuit terminates on equipment whose terminals are not marked with a temperature rating. Which column of Table 310.16 must be used to select the conductor?
- 4106An 8 AWG copper THHN conductor connects to terminals rated 75 C on both ends. What ampacity may be used for the circuit?
- 4107For a circuit rated over 100 amperes with conductors larger than 1 AWG, which temperature column may be used for termination purposes unless equipment is marked otherwise?
- 4108When 90 C rated THHN conductors are installed with 75 C terminations, what is the 90 C ampacity used for?
- 4109How may a 10 AWG grounded conductor be identified?
- 4110A 2 AWG grounded conductor has black insulation. How may it be identified as the grounded conductor?