Question 4109 of 790 · California General Electrician Exam
How may a 10 AWG grounded conductor be identified?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4109
- C: Continuous white or gray outer finish, or three white or gray stripes
Explanation
200.6(A) requires grounded conductors 6 AWG or smaller to be identified by a continuous white or gray outer finish, or by three continuous white or gray stripes on other than green insulation. Marking with tape at terminations is reserved for larger conductors.