Question 4110 of 1003 · California General Electrician Exam
A 2 AWG grounded conductor has black insulation. How may it be identified as the grounded conductor?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4110
- D: With a distinctive white or gray marking at its terminations
Explanation
200.6(B) permits grounded conductors larger than 6 AWG to be identified by a distinctive white or gray marking at their terminations at the time of installation. The marking must encircle the conductor or insulation.
More questions: Branch Circuits, GFCI and AFCI
- 4111A building has both 480Y/277-volt and 208Y/120-volt branch circuits. What is required for the ungrounded branch circuit conductors?
- 4112A white conductor in a cable assembly is used as an ungrounded conductor for a switch loop. What does the NEC require?
- 4001In a dwelling unit, GFCI protection is required for all 125-volt through 250-volt receptacles installed in which of the following locations?
- 4002A receptacle in a dwelling unit bedroom is installed 5 ft from the top inside edge of the bowl of a bar sink. Is GFCI protection required?
- 4003In a dwelling unit, receptacles within what distance of the outside edge of a bathtub or shower stall require GFCI protection?
- 4004A 240-volt, 30-ampere receptacle for an electric clothes dryer is installed in the laundry area of a single-family dwelling. Does it require GFCI protection?