An 8 AWG copper THHN conductor connects to terminals rated 75 C on both ends. What ampacity may be used for the circuit?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4106
- A: 50 amperes
Explanation
8 AWG copper is 40 A at 60 C, 50 A at 75 C and 55 A at 90 C. The 90 C insulation does not help because the 75 C terminals limit the conductor to 50 A under 110.14(C).