Question 4089 of 790 · California General Electrician Exam

A branch circuit supplies 24 amperes of continuous load and 6 amperes of noncontinuous load. What is the minimum standard overcurrent device rating?

Exactly one answer is correct.

Show solution

Correct answer to question 4089

  • A: 40 amperes

Explanation

210.20(A) requires the overcurrent device to be at least 125 percent of the continuous load plus the noncontinuous load: 24 A x 1.25 = 30 A, plus 6 A = 36 A. The next standard size at or above 36 A in 240.6 is 40 A.

Next to question ›