A multiwire branch circuit supplies receptacles in a dwelling. What does the NEC require at the point where the branch circuit originates?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4094
- C: A means to simultaneously disconnect all ungrounded conductors
Explanation
210.4(B) requires each multiwire branch circuit to be provided with a means that will simultaneously disconnect all ungrounded conductors where the circuit originates. A 2-pole breaker or identified handle ties on single-pole breakers meet this rule.