In a dwelling unit, a 30-ampere branch circuit is permitted to supply which of the following?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4087
- B: Utilization equipment such as a clothes dryer
Explanation
210.23 permits a 30-ampere branch circuit to supply fixed lighting with heavy-duty lampholders only in other than dwelling units, or utilization equipment in any occupancy. A dryer on a 30-ampere circuit is a typical example.