Question 3005 of 790 · California General Electrician Exam
When may a feeder OCPD be sized at 100 percent of the continuous load?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3005
- C: When the assembly and its OCPD are listed for operation at 100 percent of their rating
Explanation
The exception allows 100 percent sizing only where the assembly, including the OCPD, is listed for continuous operation at 100 percent of its rating. See 215.3 Exception.
More questions: Feeders and Overcurrent Protection