The available fault current at a panelboard is 18,000 A. Which breaker interrupting rating is acceptable?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3007
- D: 22,000 A
Explanation
The interrupting rating must be at least equal to the available fault current at the line terminals. Only 22,000 A meets or exceeds 18,000 A. See 110.9.