Question 3009 of 790 · California General Electrician Exam
A feeder is protected at 400 A. What is the minimum copper THWN tap conductor at 75 degrees C for a 25 ft tap?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3009
- D: 1/0 AWG
Explanation
One-third of 400 A is about 133 A. From Table 310.16, 75 degree C column, 1 AWG copper is 130 A, too small, and 1/0 copper is 150 A. See 240.21(B)(2).