Question 3011 of 790 · California General Electrician Exam
A 400 A feeder OCPD protects a feeder. Field-installed 10 ft tap conductors leave the enclosure. What is the minimum tap ampacity?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3011
- B: 40 A
Explanation
One-tenth of 400 A is 40 A. The tap must also be at least the combined calculated load and not less than the rating of the device it supplies. See 240.21(B)(1).
More questions: Feeders and Overcurrent Protection
- 3012In other than dwelling units, service equipment must be field marked with what information?
- 3013How long must a load run to be considered a continuous load?
- 3014Which of the following is not a standard ampere rating for an inverse time circuit breaker?
- 3015Under the 25 ft feeder tap rule, what minimum ampacity must the tap conductors have?
- 3016In a dwelling unit, in which location are OCPDs prohibited?
- 3017Which situation is an exception to the small conductor rule?