Question 3017 of 790 · California General Electrician Exam
Which situation is an exception to the small conductor rule?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3017
- D: Motor branch circuits protected per Article 430
Explanation
The limits of 240.4(D) do not apply where other articles specifically permit otherwise, such as motor and motor-control circuits in Article 430 and air-conditioning equipment in Article 440. See 240.4(G).