Question 3018 of 790 · California General Electrician Exam

Transformer secondary conductors not over 25 ft long must have an ampacity of at least what value?

Exactly one answer is correct.

Show solution

Correct answer to question 3018

  • D: One-third of the primary OCPD rating multiplied by the primary-to-secondary voltage ratio

Explanation

For secondary conductors up to 25 ft, the ampacity must be at least one-third of the primary OCPD rating times the primary-to-secondary voltage ratio. They must terminate in a single breaker or set of fuses. See 240.21(C)(6).

Next to question ›