Question 3012 of 790 · California General Electrician Exam
In other than dwelling units, service equipment must be field marked with what information?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3012
- B: The available fault current and the date it was calculated
Explanation
Service equipment in other than dwelling units must be legibly field marked with the maximum available fault current and the date of the calculation. The marking must be updated when changes increase the fault current. See 110.24.
More questions: Feeders and Overcurrent Protection
- 3013How long must a load run to be considered a continuous load?
- 3014Which of the following is not a standard ampere rating for an inverse time circuit breaker?
- 3015Under the 25 ft feeder tap rule, what minimum ampacity must the tap conductors have?
- 3016In a dwelling unit, in which location are OCPDs prohibited?
- 3017Which situation is an exception to the small conductor rule?
- 3018Transformer secondary conductors not over 25 ft long must have an ampacity of at least what value?