Question 2045 of 790 · California General Electrician Exam
Overhead service conductors operating at more than 300 volts to ground pass over a residential driveway. What is the minimum vertical clearance?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2045
- A: 15 ft
Explanation
Where the voltage exceeds 300 volts to ground, the clearance over residential property, driveways and commercial areas not subject to truck traffic rises from 12 ft to 15 ft. Note that a 480Y/277 volt system is only 277 volts to ground, so it would still fall under the 12 ft value. See 230.24(B).
More questions: Services and Service Equipment
- 2046Which edition of the NEC first required an outdoor emergency disconnect for one- and two-family dwelling services?
- 2047Which of the following is permitted to be connected on the supply side of the service disconnecting means?
- 2048Which situation permits an additional service to a building?
- 2049Using the 83 percent rule of the 2020 and 2023 NEC, what minimum copper THWN conductor at 75 degrees C is needed for a 200 A, 120/240 volt one-family dwelling service?
- 2050A service drop cable with a bare messenger operates at 120/240 volts. What is the minimum clearance above a sidewalk accessible only to pedestrians?
- 2051At a supply voltage of 1000 volts or less, additional services are permitted for capacity reasons when the load exceeds what value?