Which situation permits an additional service to a building?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2048
- C: A separate service for a fire pump
Explanation
Additional services are permitted for special conditions, including fire pumps, emergency and standby systems, parallel power production and similar systems. Load type or a full panelboard is not a reason for a second service. See 230.2(A).
More questions: Services and Service Equipment