Question 2047 of 790 · California General Electrician Exam
Which of the following is permitted to be connected on the supply side of the service disconnecting means?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2047
- D: A meter
Explanation
Only specific equipment may be installed ahead of the service disconnect, including cable limiters, meters, meter disconnect switches, instrument transformers and surge protective devices. General branch circuits are not on the list. See 230.82.