At a supply voltage of 1000 volts or less, additional services are permitted for capacity reasons when the load exceeds what value?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2051
- D: 2000 amperes
Explanation
Capacity requirements in excess of 2000 amperes at 1000 volts or less allow additional services. Single-phase loads above the utility's normal capacity can also qualify. See 230.2(C).
More questions: Services and Service Equipment
- 2052A service disconnect supplies only two 2-wire branch circuits. What is its minimum rating?
- 2053What is the minimum depth of working space in front of a 120/240 volt panelboard with live parts on one side and no grounded parts on the other (Condition 1)?
- 2056How is the overcurrent protection for each ungrounded service conductor generally sized?
- 2057What is the maximum number of disconnects permitted for a building supplied by one outside feeder?
- 2058What is the minimum height above finished grade for the point of attachment of a service drop to a building?
- 2059Ground-fault protection of equipment is required for a service disconnect rated 1200 A on which system?