A 480Y/277 volt switchboard faces a concrete wall (Condition 2). What is the minimum depth of the working space?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2044
- B: 3 ft 6 in.
Explanation
A 480Y/277 volt system is 277 volts to ground, where the depth is 3 ft for Condition 1, 3 ft 6 in. for Condition 2 and 4 ft for Condition 3. Concrete is considered grounded, which makes this Condition 2. See Table 110.26(A)(1).