Question 2041 of 790 · California General Electrician Exam
A detached building is supplied by one feeder. Where must its building disconnecting means be located?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2041
- A: Outside, or inside nearest the point of entrance of the feeder conductors
Explanation
A building supplied by a feeder needs its own disconnect, readily accessible and located outside or inside nearest the point of entrance of the conductors. See 225.31 and 225.32.
More questions: Services and Service Equipment
- 2042Where may the service disconnecting means for a commercial building be installed?
- 2044A 480Y/277 volt switchboard faces a concrete wall (Condition 2). What is the minimum depth of the working space?
- 2045Overhead service conductors operating at more than 300 volts to ground pass over a residential driveway. What is the minimum vertical clearance?
- 2046Which edition of the NEC first required an outdoor emergency disconnect for one- and two-family dwelling services?
- 2047Which of the following is permitted to be connected on the supply side of the service disconnecting means?
- 2048Which situation permits an additional service to a building?