Where must the disconnecting means for an outdoor air conditioning condenser be located?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8041
- C: Within sight from and readily accessible from the equipment
Explanation
Section 440.14 requires the disconnect for air conditioning or refrigerating equipment to be located within sight from and readily accessible from the equipment. Within sight means visible and not more than 50 ft away.