An air conditioning unit nameplate shows a maximum overcurrent protection (MOCP) of 40 A. What breaker is permitted?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8040
- B: Any size up to and including 40 A, as marked
Explanation
Under 440.22 and 110.3(B), the branch-circuit protective device may not exceed the maximum marked on the equipment nameplate. A 40 A MOCP means a 40 A device or smaller that still allows the unit to start.