May the HVAC service receptacle be connected to the load side of the equipment disconnecting means?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8045
- B: No, it may not be on the load side of the equipment disconnect
Explanation
Section 210.63 prohibits connecting the service receptacle to the load side of the equipment disconnecting means. Otherwise the receptacle would be dead whenever the unit is switched off for service.