Conductors from generator terminals to the first overcurrent device must have an ampacity of at least what?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8052
- A: 115 percent of the generator nameplate current
Explanation
Section 445.13(A) requires conductors from the generator output terminals to the first distribution device containing overcurrent protection to have an ampacity of at least 115 percent of the nameplate current rating. Neutral conductors may be sized under 220.61 (120.61 in NEC 2026).