Correct answer to question 8043
- D: 25 ft
Explanation
Section 210.63 requires a 125 volt, single-phase, 15 or 20 ampere receptacle outlet for servicing heating, air conditioning and refrigeration equipment. It must be readily accessible and within 25 ft of the equipment.