How is the maximum feeder short-circuit and ground-fault protective device for a motor feeder determined?

Exactly one answer is correct.

Show solution

Correct answer to question 8036

  • C: The largest branch-circuit device rating plus the sum of FLCs of the other motors

Explanation

Section 430.62(A) limits the feeder device to the largest rating of any branch-circuit short-circuit and ground-fault device in the group plus the sum of the full-load currents of the other motors. Unlike branch circuits, the feeder rule does not allow rounding up.