A motor control circuit has one side grounded. How must the circuit be arranged?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8029
- D: So an accidental ground in the control wiring will not start the motor or bypass safety devices
Explanation
Section 430.74(A) requires grounded control circuits to be designed so that an accidental ground in the control devices or wiring will not start the motor or bypass manually operated shutdown devices or automatic safety shutdown devices.