Question 8034 of 790 · California General Electrician Exam
Feeder conductors supplying several motors must have an ampacity of at least what?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8034
- D: 125 percent of the largest motor FLC plus the sum of the FLCs of the other motors
Explanation
Section 430.24 requires 125 percent of the full-load current of the highest rated motor plus the sum of the full-load currents of the other motors. Other loads are added as their own rules require.
More questions: Motors, HVAC, Generators and Transformers
- 8035A feeder supplies three motors with table FLCs of 40 A, 20 A and 10 A. What is the minimum feeder conductor ampacity?
- 8036How is the maximum feeder short-circuit and ground-fault protective device for a motor feeder determined?
- 8037The largest motor on a feeder has a 100 A branch-circuit breaker. The other motors have FLCs of 20 A and 10 A. What is the maximum standard feeder breaker size?
- 8038When may several motors be connected to a single branch circuit?
- 8039Which nameplate value is used to size branch-circuit conductors for a packaged air conditioning unit?
- 8040An air conditioning unit nameplate shows a maximum overcurrent protection (MOCP) of 40 A. What breaker is permitted?