Question 8030 of 790 · California General Electrician Exam
Under the 2023 NEC, where are the general rules for Class 1 remote-control and signaling circuits, such as many motor control circuits, located?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8030
- A: Article 724
Explanation
The 2023 NEC split former Article 725 and moved Class 1 circuits to the new Article 724, while Class 2 and Class 3 circuits stayed in 725. Motor control circuits remain covered by 430 Part VI.
More questions: Motors, HVAC, Generators and Transformers
- 8032What does the code letter on a motor nameplate indicate?
- 8034Feeder conductors supplying several motors must have an ampacity of at least what?
- 8035A feeder supplies three motors with table FLCs of 40 A, 20 A and 10 A. What is the minimum feeder conductor ampacity?
- 8036How is the maximum feeder short-circuit and ground-fault protective device for a motor feeder determined?
- 8037The largest motor on a feeder has a 100 A branch-circuit breaker. The other motors have FLCs of 20 A and 10 A. What is the maximum standard feeder breaker size?
- 8038When may several motors be connected to a single branch circuit?