Question 5040 of 790 · California General Electrician Exam
A 1200 A feeder is run in four parallel raceways, each with its own copper EGC. What is the minimum EGC in each raceway?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5040
- D: 3/0 AWG in each raceway
Explanation
Where conductors are paralleled in multiple raceways, the EGC in each raceway must be full size based on the feeder OCPD per Table 250.122. For 1200 A that is 3/0 copper in each raceway. See 250.122(F).
More questions: Grounding and Bonding
- 5041The EGC for a motor branch circuit is sized from Table 250.122 based on
- 5042Which of the following is recognized as an equipment grounding conductor?
- 5043Listed flexible metal conduit with listed fittings may serve as the EGC only where the circuit OCPD is rated not more than
- 5045Why is the earth not permitted as the effective ground-fault current path?
- 5046A ground rod is driven at a parking lot light pole and connected to the pole. How does the Code treat this rod?
- 5047Which identification is NOT permitted for an equipment grounding conductor of 6 AWG or smaller?