A 60 A circuit is upsized from 6 AWG to 4 AWG copper for voltage drop. What is the minimum copper EGC?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5039
- C: 8 AWG
Explanation
Table 250.122 gives 10 AWG for 60 A. The increase ratio is 41,740 / 26,240 = 1.59, and 10,380 x 1.59 = about 16,500 cmil, which is 8 AWG. See 250.122(B).