Question 5034 of 790 · California General Electrician Exam
For a grounded service, the GEC connection to the grounded service conductor is permitted
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5034
- B: Anywhere from the load end of the service drop or lateral up to the service disconnect
Explanation
The connection must be made at an accessible point from the load end of the overhead or underground service conductors up to and including the terminal or bus where the grounded conductor connects at the service disconnecting means. See 250.24(A)(1).
More questions: Grounding and Bonding
- 5035What is the minimum copper equipment grounding conductor for a circuit protected by a 20 A OCPD?
- 5036What is the minimum copper equipment grounding conductor for a feeder protected by a 100 A OCPD?
- 5037What is the minimum copper equipment grounding conductor for a feeder protected by a 400 A OCPD?
- 5038A 20 A branch circuit is upsized from 12 AWG to 10 AWG copper to limit voltage drop. What is the minimum copper EGC?
- 5039A 60 A circuit is upsized from 6 AWG to 4 AWG copper for voltage drop. What is the minimum copper EGC?
- 5040A 1200 A feeder is run in four parallel raceways, each with its own copper EGC. What is the minimum EGC in each raceway?