Question 5037 of 790 · California General Electrician Exam
What is the minimum copper equipment grounding conductor for a feeder protected by a 400 A OCPD?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5037
- A: 3 AWG
Explanation
Table 250.122 requires at least 3 AWG copper for OCPDs rated 400 A. The EGC is sized on the OCPD rating, not on the conductor ampacity.
More questions: Grounding and Bonding
- 5038A 20 A branch circuit is upsized from 12 AWG to 10 AWG copper to limit voltage drop. What is the minimum copper EGC?
- 5039A 60 A circuit is upsized from 6 AWG to 4 AWG copper for voltage drop. What is the minimum copper EGC?
- 5040A 1200 A feeder is run in four parallel raceways, each with its own copper EGC. What is the minimum EGC in each raceway?
- 5041The EGC for a motor branch circuit is sized from Table 250.122 based on
- 5042Which of the following is recognized as an equipment grounding conductor?
- 5043Listed flexible metal conduit with listed fittings may serve as the EGC only where the circuit OCPD is rated not more than