Question 3034 of 925 · California General Electrician Exam
Under the 2023 and 2026 NEC, what is required for a feeder supplying distribution equipment in a dwelling unit?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3034
- D: A surge protective device in or next to the feeder-supplied distribution equipment
Explanation
Section 215.18, new in 2023, requires a Type 1 or Type 2 SPD in or adjacent to distribution equipment supplied by a feeder in dwelling units and similar sleeping occupancies, unless the upstream protection arrangement covers it. The SPD needs a nominal discharge current rating of at least 10 kA.
More questions: Feeders and Overcurrent Protection
- 3035A feeder supplies a continuous load of 160 A only. What is the minimum rating of the feeder OCPD, assuming standard equipment not rated for 100 percent operation?
- 3036In a multi-tenant building, who must have ready access to the OCPDs protecting the conductors supplying a tenant space?
- 3037Arc energy reduction is required where the highest continuous current trip setting of a circuit breaker is at least what value?
- 3039May an OCPD be placed in a grounded conductor?
- 3040Which statement about supplementary OCPDs is correct?
- 3041Unless specifically permitted elsewhere, what is the maximum OCPD for 10 AWG aluminum conductors?