Question 3040 of 790 · California General Electrician Exam
Which statement about supplementary OCPDs is correct?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3040
- B: They are not required to be readily accessible
Explanation
Supplementary overcurrent devices are not required to be readily accessible. This is listed as an exception to the readily accessible rule. See 240.10 and 240.24(A).
More questions: Feeders and Overcurrent Protection
- 3041Unless specifically permitted elsewhere, what is the maximum OCPD for 10 AWG aluminum conductors?
- 3042How must a 25 ft feeder tap terminate?
- 3043What is the general rule for the location of OCPDs?
- 3044A building main disconnect, not the service disconnect, is rated 1200 A on a 480Y/277 volt system. What does the NEC require?
- 3045A 120/240 volt slash rated circuit breaker may be used on which system?
- 3046Where a premises has feeders supplied from more than one nominal voltage system, how must the ungrounded feeder conductors be identified?